    February 26, 2019 at 5:08 pm

    Hello,

    Ok i found the problem…

    The cable must be isolated because there is an interference.

    Maybe with a shielded cable.

    The controllino is in an electrical cabinet installed an the sensor cable go with an cable bundle.

    So, after test, there no problem anymore. maybe it is for that.

    If not i will come back.

    Thank you all for assistance and quick response ! :)

    Have a nice day.

    Best Regards.

  • pg067

    Member
    February 26, 2019 at 1:01 pm

    I have the same problem but with the pinHeader 5v it ok and work fine.

    When i put the 24V in, the sensor goes to-127deg ?

    I do not understand why ?

    Some other ideas ?

    Thank you very much for the help.

    Best Regards.