Hello, I had exactly the same problem so I think this might not be a hardware defect. However, I did not pursue solving this problem any further but managed to find a workaround (not using the analog out pins) for my specific problem. So, if you managed to find a solution, I would be happy to let us know.
Best regards,
niellsonn
-
Hello, I also had the same problem. I contacted the manufacturer and the issue is not a hardware defect, rather a production error. The outputs were configured for 0-20mA instead of 0-10V. If you follow the website tutorial below, you should find that the 0 ohm resistors are missing. So to change the MAXI outputs to 0-10V simply add a solder bridge where the 0 ohm resistors are supposed to be. This fixed the issue for me.
Website tutorial:
https://www.controllino.biz/knowledge-base/current-outputs-maxi-automation/ Regards,
Ethan
-
Sorry for the late response. Yes! That was the same problem for my Controllino. The 0 Ohm Resistors were missing. So this wasn’t a technical or software issue, but a manufacturing issue.
I would suggest to replace the resistors by jumpers. Thats would make switching between voltage and current output easier.